Per ASHRAE 62.1-2007, the outside air requirements can change based on the time of year, s well as the supply and return diffuser locations. Well at least in the North here, it's common. The zone air distribution effectiveness can change, causing the amount of outside air required to change.
With a rooftop unit the air is probably supplied and returned in the ceiling. Cold air supplied from the ceiling and returned at the ceiling has an effectiveness of 1.0. Warm air supplied at more than 15 degrees F warmer than return will have an effectiveness of 0.8. This means that more outside air is required in the winter than in the summer (stratification).
I designed a VAV AHU system for a building, where the winter outside air requirement equaled the total supply air (VAV reheat volume), and the summer outside air requirement was less than the winter outside air requirement. Both conditions were calculated in the 62MZCalc spreadsheet and documented to prove the results.
In figuring out your ventilation calculations, find and read ASHRAE 62.1-2004. Then read it again. Then read it as you are trying to calculate. Most state codes, if not all by now, utilize the ASHRAE method, or allow an engineered calculation as an alternative to the state requirements.