I am the HVAC designer for my engineering firm, and we frequently come across VAV systems in medical office buildings that pose a unique problem. Based on heat loads and standard practices, we supply enough flowrate to each room to cool the space using the 400 CFM per ton rule of thumb. However, based on ASHRAE standards, office spaces require a minimum of 4 air changes per hour. When we are dealing with a VAV system that is only capable of supplying 57 degree 50% humidity air, how does one design for the correct amount of air changes without over cooling the space? Also, how do you handle the outside air requirements given you can only provide air from the main loop. IS it a safe assumption to exhaust the amount of O.A. you need and make sure the AHU for the entire floor is pulling in enough O.A. to cover the difference? Thanks for the help!