ajlimuran
Industrial
- Aug 22, 2014
- 16
To All Experts,
Specs of the VCB are below;
VD4 ABB - 17.5 KV/630 Amperes/ 25 KA
Our plant is diesel/bunker C power plant supply the small island. The unit is status is on going commissioning and it is synchronize to the grid.
The diesel generator rated 13.8 KV and 2.1 MW capacity connected to generator breaker and bus then, taking off to the feeder line to utility network.
It were happened 4 times explosions, below are the sequence of events;
1. First , the DG was synchronized and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We neglect to check the internal of VCB and replaced it nee VCB and PT fuses.
2. Second , again the unit is synchronized and and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We neglect to check the internal of VCB and replaced it nee VCB and new PT ans fuses again.
3. Third , again the unit is synchronized and and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We check the VCB all replaced then we found out the the caused of flashover and switchgear explosion is from the VCB. And, why that the only damage and failed bottom contact of the VCB is only phase B among the 3 and Phase A & C is is not damages.
My questions now, is what would be the cause of series of failure of the VCB.
Before we instaled was the insulation resistance in the bottom is 200 Mega ohms respectively while the top terminal is in 3 giga ohms.
Please help.
Specs of the VCB are below;
VD4 ABB - 17.5 KV/630 Amperes/ 25 KA
Our plant is diesel/bunker C power plant supply the small island. The unit is status is on going commissioning and it is synchronize to the grid.
The diesel generator rated 13.8 KV and 2.1 MW capacity connected to generator breaker and bus then, taking off to the feeder line to utility network.
It were happened 4 times explosions, below are the sequence of events;
1. First , the DG was synchronized and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We neglect to check the internal of VCB and replaced it nee VCB and PT fuses.
2. Second , again the unit is synchronized and and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We neglect to check the internal of VCB and replaced it nee VCB and new PT ans fuses again.
3. Third , again the unit is synchronized and and run 2-3 hours and switch gear explosion and DG tripped with the indication of 51V and 87G.
After explosion , my team checked and it was found out the the PT fuse blown and flash over evidence observe in the PT and VCB.
We check the VCB all replaced then we found out the the caused of flashover and switchgear explosion is from the VCB. And, why that the only damage and failed bottom contact of the VCB is only phase B among the 3 and Phase A & C is is not damages.
My questions now, is what would be the cause of series of failure of the VCB.
Before we instaled was the insulation resistance in the bottom is 200 Mega ohms respectively while the top terminal is in 3 giga ohms.
Please help.