Ventilation/construction requirements

Status
Not open for further replies.

edmenold

Mechanical
Oct 1, 2008
3
0
0
US
Thank you in advance!!

Have a client (in house eng)who is installing an enhanced walk in oven. Disagreement over construction standards.


stats:

480v/3ph/6o hz---115 amps-oven
recirculating 7,000 CFM @ 7 1/2 HP fan motor
exhaust-600 CFM @ 1/2 HP fan motor

TEMP- 500 deg F maximum
150 to 350 deg F normal operating temp
75 deg F above ambient minimum.

I suggest single wall spiral (incorporate a high temp flex connection)with a double wall posi vent thru roof with stack terminating +/- 6'-0" above roof line. Exhaust duct would be under positive pressure. This would meet NFPA 70 & 86. verus a welded schedule 40 pipe run (his Idea).

Please comment.
 
Replies continue below

Recommended for you

NFPA 86 refers to 91 refers to SMACNA and none say exactly what needs to be done for oven exhaust (far as I could see). I think I'd side with you. You want a double wall, not just a sched. 40 iron pipe...
 