We have a design that seems solid but have come up against this problem with the exhaust fans that are installed. The space is ventilated at 12 air changes per hour, exhaust is ducted high and low within the space, make up air is 10% less to create a negitive, system is controlled low ventilation rate (about 8 AC) occupied and high (12 AC) on gas detection. Here is the issue:
Exhaust fans are sidewall mounted, outdoor spun aluminum with motor out of the air stream. Electical contractor will not hook up the fan as he can see the motor is not rated for class 1 div one area like all of the other electrical on the inside of the building.
Question #1:
If the motor is out of the air stream are we good?
Question #2:
If there is a clearance rule from the discharge of the fan what is it?
thx!!