Venturi Vacuum

Status
Not open for further replies.

Speedy

Mechanical
Jun 5, 2001
229
I have an application where I want to confirm air-flow in an extraction duct. At present we use a diaphragm type vacuum switch which measures the vacuum from a smaller L-shaped pipe fixed in the middle of the air flow, i.e the venturi principle.

The vacuum switch is unreliable. I have measured the vacuum at 55mm water. This with a simple water tube. This equates to 5.5 milibar (if my calculations are correct).
The range on the vac switch is 5~50 milibar.

My question is how can I increase the vacuum to bring it closer to the switch mid-range?

Would a funnel type opening on the end of the venturi pipe help?

Regards,
Speedy

[roll1][roll1][roll1]
 
Replies continue below

Recommended for you

Speedy, what you describe is a Pitot tube, not a venturi. Are you sensing differential pressure between the tip of the Pitot tube and the wall of the duct. If not, static pressure changes in the duct will affect your reading.
 
More correctly, it sounds like a total pressure probe.

If you simply need to know flow or no flow, a sail switch might be a better choice.
 
Thanks for your replies.

To clarify - it is in fact a pitot tube, with no static pressure measurement. It's function is to clarify FLOW / No FLOW.

I like the idea of a sail switch, but I have to find one with ATEX approval.

Any suggestions,
Speedy
 