I've reviewed the text from "The Analysis of Irregular Shaped Structures" and it briefly talks about vertical offsets in building chords. However, there isn't much discussion on how to design or detail this condition for different scenarios.
In the image below, I have a rectangular shaped building. The following is assumed for the point of this discussion:
[ul]
[li]Diaphragm is flexible.[/li]
[li]Diaphragm shear is transferred directly to the top of the perimeter tie-beam.[/li]
[li]Lateral load in each north/south & west/east direction is the same unit value at 400 PLF.[/li]
[li]There is a 3ft vertical offset at the tie-beam, along line B, from the center of the building due east. No other vertical offsets occur.[/li]
[li]Plane of the roof diaphragm is the same at all locations (ignore slope requirements) of the building via varying truss heel heights. There exists proper detailing to transfer all loads to top of tie-beam as previously mentioned.[/li]
[li]South elevation has (2) openings separated by a CIP concrete column. Left side has a shear wall. The only lateral force resisting components along line B are the shear wall and tie-beam system.[/li]
[li]All other exterior lines have adequate shear walls.[/li]
[/ul]
Question #1:
For transverse wind (north/south) the maximum chord force in lines A and B is:
400lb/ft x (30ft)²/ (8 x 25ft) = 1,800 lb
How is this chord force transferred across the vertical step in the tie-beam?
Question #2:
For longitudinal wind due east, the tie-beam is acting as a drag that is pulling away from the shear wall.
Diaphragm shear at line B = 400lb/ft x (25ft /2) = 5,000 lb
Shear in wall directly from the diaphragm = 2,000 lb
Drag force at 1.4 is 3,000 lb tension (due east)
(This sums to the total lateral force of 5,000 lb)
Drag force in tie-beam at 1.5 is approximately 2,500 lb tension (due east)
Similar to Question #1, how is the drag load continuous at the step in the tie-beam?