It would be nice if NFPA did state it more definitively (if it is in fact the intent), however there are a few sections that lead me to this conclusion.
Commentary under section 8.5.5.3.2. in the NFPA 13 2013 Handbook says:
"Does NFPA 13 consider overhead doors an obstruction?
It is important to stress that overhead doors are considered an obstruction (see 8.5.5.3.1). Although the overhead door is not considered an obstruction when in the closed position, as shown in Exhibit 8.12, the discharge from the sprinkler over the door will be obstructed when the door is in the open position. Sprinklers need to be positioned so that their discharge can adequately reach under the overhead door. The 1999 edition of NFPA 13 was revised to specifically allow the use of sidewall sprinklers for these applications. [See 8.4.2(3).]"
Also, section 8.7.3.1.7 provides specific criteria for sidewall sprinklers in ordinary hazard occupancies to use light hazard spacing for under overhead doors. Which would seem to give weight that the allowance for using sidewall sprinklers under overhead doors only. As in I would think one would have a hard time justifying using light hazard spacing of sidewalls under runs of ducts/other obstruction types so I would likewise think it a stretch to take the allowance for SWs to be used for under obstructions that are not overhead doors. The provisions for use of SWs under overhead doors seems to be very specific to overhead doors and not necessarily to be used as a go ahead for using under obstructions in general.
Commentary in the Handbook to section 8.7.3.1.7 states 'Sprinkler protection is required under overhead doors so that protection is provided when the doors are open and the ceiling sprinklers are obstructed. In ordinary hazard areas, this provision permits larger doors to be protected by a single sidewall sprinkler, reducing the installation costs while not significantly impacting the protection of the space.
Again, that seems to be providing very specific to overhead doors.
In looking at the handbook it states in regards to 8.7.5.2 'Obstructions to Sprinkler Discharge Pattern Development.' (8.7 being for sidewalls...)
"Sidewall sprinklers, like upright and pendent sprinklers, must be located to avoid obstructions that affect the discharge pattern development or prevent the discharge from reaching the protected hazard. Paragraphs 8.7.5.2 through 8.7.5.3 on obstructions are similar in content to those for upright and pendent sprinklers in 8.6.5.2 through 8.6.5.3. Rather than assume that these types of obstructions do not exist, these requirements are included in NFPA 13 to address what to do when these obstructions are encountered. Other types of sprinklers, such as upright or pendent sprinklers, should be used if the obstruction cannot be relocated, or if the sidewall sprinkler cannot be repositioned along the wall to avoid the obstruction."
I have seen others installations where they have installed ECHSW at 24’ spacing under runs of ducts. It would seem that there would have to be a huge fire before those sprinklers activate. I know FM have drastically revised their criteria for under obstruction protection (with the criteria in FM 2-0) where they have reduced the allowable spacing under obstructions so that the sprinkler will be close enough to the plume of the fire to activate.
Also in regards to CKCECB’s post, it would seem that the mixing of Standard Response and Quick Response would be a violation of NFPA 13 2013 section 8.3.3.2
CKCECB, is the project NFPA? What hazard classification is the room being considered?