I've got an old granulator with what I believe to be around a 20 horse motor on it, 575V 3 phase, 20 or 30 years old, or older maybe. The ID plate is no longer legible.
I put a fuse block in for 30A CC time-delay fuses, midget size, and this motor blows them like popcorn.
The motor only draws 11A when running, and the fuses are rated for 150A for at least 10 seconds, so I was amazed when the fuses blew. I put a meter on the motor lines and found that the inrush current is 165A.
I did a megger test and the motor passed without trouble. The amperage isn't perfectly even, ranging from 9.7A to 11.2QA, but this amount of inrush has me baffled.
I can switch to RK5 fuses so I can put 40A fuses on there, but then I have to change the wire gage, etc.
Can anyone suggest why the inrush current is so high for this motor?
Mike
I put a fuse block in for 30A CC time-delay fuses, midget size, and this motor blows them like popcorn.
The motor only draws 11A when running, and the fuses are rated for 150A for at least 10 seconds, so I was amazed when the fuses blew. I put a meter on the motor lines and found that the inrush current is 165A.
I did a megger test and the motor passed without trouble. The amperage isn't perfectly even, ranging from 9.7A to 11.2QA, but this amount of inrush has me baffled.
I can switch to RK5 fuses so I can put 40A fuses on there, but then I have to change the wire gage, etc.
Can anyone suggest why the inrush current is so high for this motor?
Mike