Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

Very Tough Flow Application - Help!

Status
Not open for further replies.

Chinook82

Industrial
Sep 26, 2003
21
0
0
I have the attached flow application and can only come up with a double/triple D/P solution. Any better ideas?

Thanks very much.

 
Replies continue below

Recommended for you

Perhaps your issues relate to the high flow rate and density turndown. Coriolis meters could help with some of the problems. What accuracy is required at each end of the flow spectrum?
 
Yes the turndown of just under 600:1 is the problem. At first I wanted to go with thermal mass but the steam portion seems to stop the suppliers. At the low end I would like +/- 2% accuracy.

Thanks again, Dave
 
Consider two parallel Coriolis meters of different sizes; and a switching valve to select one or both based upon the flow rate through the smaller meter.
 
I'm not understanding the problem here. Is the 101.36 kPa (a) upstream or downstream pressure? In either case, the 38% steam would condense at that temperature and pressure and you'd have water and CO2 or water and N2. I have to assume that the only pressure you mentioned is downstream and you have some room to play with pressure upstream (without that assumption, this problem has no solution).

Since you posted it in Measurement, I'll assume you are trying to measure this stuff with a 600:1 volume turndown. The only way I know of to get that kind of range is with a critical flow nozzle--use something like a V-cone or a Taylor Choke in front of a critical flow nozzle and build a table for the RTU that XX press upstream of the nozzle is YY kg/hr. Your +/- 2% with 600:1 volume turndown is quite doable.

David
 
The only way you can have 100% vapour is if the pressure is 60 kpa or the temperature is 190 C and then it may not be that because of changes in composition. The data you presented is two phase flow and the liquid phase will not have a pH of 7.0.

The only device that will measure this is a coriolis meter opr better yet two meters as JLSeagull recommended.
 
Status
Not open for further replies.
Back
Top