VFD, Active Harmonic Filter, Power Consumption???

Status
Not open for further replies.
Replies continue below

Recommended for you

A 50A rated unit in a NEMA 1 housing operating at rated current will dissipate 1800W of losses as heat.

A 50A rated type in a NEMA 12 housing operating at rated current will dissipate 2150W of losses as heat.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
I can read that much. Doesn't that mean I am using from 7% to 9% more energy?
 
No, it means that of the energy going in, that much is being lost as heat.

By the way, measure the heat loss across a restricted valve. Most of it is carries away in the fluid, but that energy is still lost, and it has to come from somewhere.
 
"No, it means that of the energy going in, that much is being lost as heat."

So to control the harmonics from a 50 amp motor, the active harmonic filter is losing 2150 watts to heat. Isn't that adding another 2.88 HP load to the system?
 
Yes, well sort of...

IF you have decided that harmonic mitigation is important to you and have decided to use a device such as that, then of the 50A going through it, up to 2150W of that energy will be lost as heat.

BUT (and this is a BIG BUT [wink]) a 50A Active Filter is not used for a 50A motor, the 50A refers to handling 50A of harmonic current, not 50A of load current. 50a of harmonic current would imply a much much bigger motor; probably in the range of 300-400HP (assuming 460V). So that "2.88HP" of losses becomes somewhat insignificant compared to the potential energy savings of using a VFD compared to throttling. As I said, think about the energy loss across a valve on a 350HP pump. Probably more than that, and all that energy had to come from the pump motor. I'm not an ME, but I'd bet it is a wash at best...

 