I appreciate everyones feedback but I still have a few open ended questions.
1. If a VFD is being used and the motor is not inverter duty should you consider a minimum class of insulation
and would it help?
2. We know there is Class B, F and H insulation classes available. We also know that <3200' elevation B should suffice in most cases. >3200' F is needed to get a B rise at altitude. >3200' H to get a F rise. But would this apply on submersibles?
3. Most submersibles come with a 1.15 SF which I surmise means it also has F rise?
4. Temperature extremes with pumpage adversely affect the motor cooling properties that can reduce the rise proportionally. I am seeing more submersbiles that are being used on VFD arrangements. I've also been told that all submersibles (3HP to 150HP) are already built to cover inverter duty operations. Have any of you found that to be different than what I've been told?
5. Most submersibles are sealed by oil chambers and mechanical seals. At least the ones I've been working on.
If the outer (lower seal) fails the oil is contaminated and it changes the oils continuity thereby setting off an alarm
feature indicating water entry. However, I've experienced a situation where the motor's inner seal failed and sucked the oil up into the winding areas. My question is will oil entry into the motor cause the motor to go to ground? Or does the motor cause fatigue to the insulation thereby causing the oil to flash? Some of the motor's I've seen have been chared and pools of oil within the chamber.
6. There seems to be a vacuum inside these motors and I don't know why it forms but one must take care when opening up a submersible during repair. I wonder if this vacuum
is sucking the oil up through the inner seal workings?
Have any of you experienced this occurrence?
Wayne E. Lovison
service-parts@naglepumps.com
1. If a VFD is being used and the motor is not inverter duty should you consider a minimum class of insulation
and would it help?
2. We know there is Class B, F and H insulation classes available. We also know that <3200' elevation B should suffice in most cases. >3200' F is needed to get a B rise at altitude. >3200' H to get a F rise. But would this apply on submersibles?
3. Most submersibles come with a 1.15 SF which I surmise means it also has F rise?
4. Temperature extremes with pumpage adversely affect the motor cooling properties that can reduce the rise proportionally. I am seeing more submersbiles that are being used on VFD arrangements. I've also been told that all submersibles (3HP to 150HP) are already built to cover inverter duty operations. Have any of you found that to be different than what I've been told?
5. Most submersibles are sealed by oil chambers and mechanical seals. At least the ones I've been working on.
If the outer (lower seal) fails the oil is contaminated and it changes the oils continuity thereby setting off an alarm
feature indicating water entry. However, I've experienced a situation where the motor's inner seal failed and sucked the oil up into the winding areas. My question is will oil entry into the motor cause the motor to go to ground? Or does the motor cause fatigue to the insulation thereby causing the oil to flash? Some of the motor's I've seen have been chared and pools of oil within the chamber.
6. There seems to be a vacuum inside these motors and I don't know why it forms but one must take care when opening up a submersible during repair. I wonder if this vacuum
is sucking the oil up through the inner seal workings?
Have any of you experienced this occurrence?