garyefficiencycnslt
Does anyone know how to answer this? I am getting widely varying answers from manufacturers reps trying to sell me results.
A warehouse freezer (-20°F) is served by four (4) evaporator coils. The full refrigeration load in the freezer is 50 tons. Each coil has four (4) fans, each driven by a 5-horsepower motor running at full speed. I am considering retrofitting the fan motors with variable frequency drives (VFDs), with a total project cost of $72,000. The refrigeration compressors serve other loads and operate at 1.8 BHP/ton. The customer’s marginal cost of electricity is $0.085 per kWh. The load profile in the freezer is as follows:
Percent of hours in year Percent of full refrigeration load
2% 100%
10% 95%
12% 90%
15% 85%
20% 80%
15% 75%
13% 70%
10% 65%
3% 60%
The facility operates continuously, except for a one-week shutdown each year.
Each coil is defrosted four (4) times per day for 30 minutes per defrost cycle.
The VFD efficiency is 96% across the range of expected operation. The fan motors are three-phase NEMA premium efficient motors with an efficiency of 90%. At full speed in this application the motors operate at a load factor of 85%. 1.What are theannual energy savings for this project (kilowatt-hours and dollars). 2. Calculate the motor speed for each part-load bin.
2% 100%
10% 95%
12% 90%
15% 85%
20% 80%
15% 75%
13% 70%
10% 65%
3% 60%