edison123
Electrical
- Oct 23, 2002
- 4,490
Motor specs - GE 440 V, 100 HP, 169 Amps, 350 RPM, 60 Hz.
Now running by VFD.
No-load volts : 188 V
No-load current : 123 A
No-load frequency : 23 Hz
Why is the no-load current nearly 73% of FLC ? I know that for 23 Hz, the voltage must be 169 V. But will a 11% volt increase change the no-load current so drastically ?
I am investigating why the drive is outputting 188 V isntead of 169 V at 23 Hz.
Now running by VFD.
No-load volts : 188 V
No-load current : 123 A
No-load frequency : 23 Hz
Why is the no-load current nearly 73% of FLC ? I know that for 23 Hz, the voltage must be 169 V. But will a 11% volt increase change the no-load current so drastically ?
I am investigating why the drive is outputting 188 V isntead of 169 V at 23 Hz.