I have a question about properly fusing VFDs. An example that has me perplexed at the moment seems to be falling in a grey area for me, as my ability to interpret NEC is lacking.
I have three 230V 1.5 HP motors with a 5.6A FLA each, to be driven from a single VFD. This would typically call for a 5HP VFD which requires 35A fuses or circuit breaker. The twist is, for this system, a high carrier is required for noise reasons. Therefore, I'm using a 10 HP drive at high carrier, which derates down to 5HP at a high carrier. This 10 HP drive calls for 60A fuses or Circuit breaker.
Is there any exception to the rules as I understand them, that says I can size my feeder circuit based on load + a percentage, vs. just sizing based on manufacturer's recommended 60A? This is a huge circuit for three 1.5 HP motors.
Thanks in advance,
~Mark
I have a question about properly fusing VFDs. An example that has me perplexed at the moment seems to be falling in a grey area for me, as my ability to interpret NEC is lacking.
I have three 230V 1.5 HP motors with a 5.6A FLA each, to be driven from a single VFD. This would typically call for a 5HP VFD which requires 35A fuses or circuit breaker. The twist is, for this system, a high carrier is required for noise reasons. Therefore, I'm using a 10 HP drive at high carrier, which derates down to 5HP at a high carrier. This 10 HP drive calls for 60A fuses or Circuit breaker.