Mila15

Electrical
Dec 19, 2012
27
I just realized that the vendor is using a thermal-magnetic breaker to feed a VFD/Motor application rated at slightly above 125% FLA. Looking at motor starting curve Vs breaker curve, it seems pretty tight. My question is, what would be the maximum starting current drawn by a 753 Powelflex? Could that ever be as large as the motor starting current? I'm at a position where I can use a larger size breaker/cable, but wanted to know if that's even a concern. Thanks in advance for your help!
 
Replies continue below

Recommended for you

The maximum that drive can put out, assuming a Heavy Duty rating, is going to be 150% current for 60 seconds, 200% for 3 seconds. That breaker should not trip on that.

Motor current, when frequency is controlled WITH voltage, can be very significantly lower than if started Across-the-line (DOL), in fact the VFD is able to make the motor put out 100% FLT at 100% FLC, no other starting method can accomplish that. VFDs are quite frequently used as glorified soft starters for that very reason.

"Will work for (the memory of) salami"
 
You don't state the drive size, but if it is a small one make sure that it either has a soft pre-charge for the DC link or that your breaker can withstand the very short inrush as the link capacitors charge up. Medium and large drives almost always have a soft pre-charge.

 
Thanks all! below are drive/motor/breaker info:
VFD: Powerflex 753 rated for 40 HP motor (52 A)
Motor: 40 HP, 46 FLA, 306 LRA
Breaker: Type HFD 3070, 70A

The AB representative confirmed jraef's statement: max of 200% of FLA during motor start, which would not trip breaker even if motor start lasted for more than 10 seconds. Are there any good documentation I can read regarding this operation?
 
Yes there is a soft pre-charge on that drive.

Lots of learning resources on VFDs out there, try searching on "VFD tutorial".