itsmoked
Electrical
- Feb 18, 2005
- 19,114
Had a guy call me about his 5HP VFD.
It's an ABB-AC35503U style running a saw.
He described it as 'acting weird'. When asked to define that he said in both vector or v/hz mode it powers up. When he starts to raise the output frequency above 0.0Hz stepping to 0.1Hz the motor goes to full rated speed (1725) immediately.
I can see some odd parameter settings possibly causing that except in his efforts to troubleshoot this he's taken the VFD and motor to other places in town and it works correctly in those locations. It only malfunctions in his shop. He went on to say he has some crazy imbalances in his power. He told PG&E about it and they came out and examined things and replaced all the transformers supplying the place!
Now his line voltages are (please sit down) 246V, 230V, 254V!!
While this truly sucks I'm still puzzled as to what a diode bridge front-end of a VFD would care about it. I can't see a reason imbalance would bother a VFD other than working the bridge diodes unevenly.
I have to pay this place a visit soon. I'll check the line voltages at the incoming service to make sure the imbalance isn't house-wiring/loading.
Anything else you folks can think of to check?
Keith Cress
kcress -
It's an ABB-AC35503U style running a saw.
He described it as 'acting weird'. When asked to define that he said in both vector or v/hz mode it powers up. When he starts to raise the output frequency above 0.0Hz stepping to 0.1Hz the motor goes to full rated speed (1725) immediately.
I can see some odd parameter settings possibly causing that except in his efforts to troubleshoot this he's taken the VFD and motor to other places in town and it works correctly in those locations. It only malfunctions in his shop. He went on to say he has some crazy imbalances in his power. He told PG&E about it and they came out and examined things and replaced all the transformers supplying the place!
Now his line voltages are (please sit down) 246V, 230V, 254V!!
While this truly sucks I'm still puzzled as to what a diode bridge front-end of a VFD would care about it. I can't see a reason imbalance would bother a VFD other than working the bridge diodes unevenly.
I have to pay this place a visit soon. I'll check the line voltages at the incoming service to make sure the imbalance isn't house-wiring/loading.
Anything else you folks can think of to check?
Keith Cress
kcress -