On 8.5MW motor vibration spikes are observing on both drive and non-drive end bearings . During spikes the motor DE/NDE bearing vibrations value exceed more than 6.3mm/s rms for very short duration and then become normal. However, the coupled compressor and gear box vibration during this period don’t show any change in vibration.
It is to note that the vibration spikes are coming during switching of loads on the same 6.6KV bus from where NGC-1 motor power is coming. During the switching of HP FWP Motor (rating 1000kW) or at the time of energization the transformer (rating: 800KVA) at no load vibration spikes are observing. The duration of vibration spikes is less than a seconds during transformer energization and in 3 seconds during HP FWP Motor Startup. Moreover, such behavior is not observing on remaining 8.5MW motors (of same manufacturer) connected on buses IB and IC.
Once same 8.5MW Motor was started but when motor started it was observed that motor was taking unbalance current . There was a difference of 60A between Phases as shown in below mention picture. The motor was stopped and inspection of motor was performed by removing all insulators as shown in pictures.
During inspection, 1 stud was found damaged which was repaired and after repaired following tests were performed in order to verify the health of motor (Report attached for reference).
1- Surge Comparison test
2- Winding resistance test
3- Insulation Resistance test.
The motor was put into operation after ensuring health of motor but again continuously vibration spikes are coming. Therefore, support is required in understanding possible reasons of stud damage and possible causes of vibration spikes on motor.
It is to note that the vibration spikes are coming during switching of loads on the same 6.6KV bus from where NGC-1 motor power is coming. During the switching of HP FWP Motor (rating 1000kW) or at the time of energization the transformer (rating: 800KVA) at no load vibration spikes are observing. The duration of vibration spikes is less than a seconds during transformer energization and in 3 seconds during HP FWP Motor Startup. Moreover, such behavior is not observing on remaining 8.5MW motors (of same manufacturer) connected on buses IB and IC.
Once same 8.5MW Motor was started but when motor started it was observed that motor was taking unbalance current . There was a difference of 60A between Phases as shown in below mention picture. The motor was stopped and inspection of motor was performed by removing all insulators as shown in pictures.
During inspection, 1 stud was found damaged which was repaired and after repaired following tests were performed in order to verify the health of motor (Report attached for reference).
1- Surge Comparison test
2- Winding resistance test
3- Insulation Resistance test.
The motor was put into operation after ensuring health of motor but again continuously vibration spikes are coming. Therefore, support is required in understanding possible reasons of stud damage and possible causes of vibration spikes on motor.