hello all,
i am running feeders to (2) 3 phase , 480V, 75HP pumps. FLA for each pump is 96A and they are located at a distance of 176 feet from the panel.
according to code:
96A * 1.25 = 120 A, then adjusting for voltage drop gives me #1/0 wires
now do i need to add derating factor if i am running feeders to both pumps in one conduit OR it is either or (voltage drop or derating but not both)? meaning one will cancel the requirement for the other?
if i have to do adjustment for derating then i ll end up with #3/0 which is too large??
thank you,