EIT231
Structural
- Apr 21, 2010
- 8
hey there and thanks in advance -
I found this article
and this problem: (480v branch ckt - uncoated copper)
Determine wire size Run a stranded copper wire 200 ft at 20A.
you can use the following method. To complete the numerator, multiply as follows: 1.73 x 212.9 ohms x 200 ft x 20A = 89371.2 Dividing the 89371.2 by the acceptable voltage drop of 14.4V gives you 6207 circular mils.
Where is the 212.9 Ohms from?
thanks
I found this article
and this problem: (480v branch ckt - uncoated copper)
Determine wire size Run a stranded copper wire 200 ft at 20A.
you can use the following method. To complete the numerator, multiply as follows: 1.73 x 212.9 ohms x 200 ft x 20A = 89371.2 Dividing the 89371.2 by the acceptable voltage drop of 14.4V gives you 6207 circular mils.
Where is the 212.9 Ohms from?
thanks