jerebear
Electrical
- Oct 1, 2007
- 13
This question is in regard to how voltage drop is calclated for a circuit from a distribution panelboard. I know how the calculation is done and that it needs to be no more than 3%. My issue is an electrical engineer that does not understand how to calculate the voltage drop for a circuit. He looks at the individual circuit, in this case a 20 amp 120 volt special purpose circuit 250' from the panelboard the total calculated load on the circuit is to be 8.75 amps. Going upstream from the panelboard there are a couple of distribuition switchboards, a 4160 substation and 4160 switchgear at the main service. In stead of calculating just the 3% voltage drop of the circuit, he is calculating 5% voltage drop from the receptacle all the way back to the main service. Now you have to take into account that he has used this same philosophy to calculate the 2% voltage drop for the feeders to all switchboards and panelboards throughout the building.
That being said, the circuit in question per his calculation is to be 2 - #4 & 1- #8 grd. The hardest one to believe is a 120 volt 20 amp circuit that is even further from the main service and is specified to be 1/0 conductors. Is there some documentation somewhere other than the NEC, that is where he is getting is reasoning, where I can show him that he is calculating this incorrectly?
That being said, the circuit in question per his calculation is to be 2 - #4 & 1- #8 grd. The hardest one to believe is a 120 volt 20 amp circuit that is even further from the main service and is specified to be 1/0 conductors. Is there some documentation somewhere other than the NEC, that is where he is getting is reasoning, where I can show him that he is calculating this incorrectly?