I have a 1/2MW Cummins generator regulator issue.
Keep in mind I have NO spec plate on the unit what-so-ever. The V12 turbo'd engine generator is 480VAC delta supplying a handful of rail cars in a seasonal (this season) application. It is not paralleled.
The existing regulator is a Basler Electric APR125-5 (giant potted brick) which is no longer available.
The replacement is a VR902 made by who-knows. ESI??
We're supposed to include a power transformer between two phases that supplies the power to the regulator for the regulator to use for the generator's excitation.
1) How do I size this thing? Since I have no measured or nameplate info on the generator's excitation range, have you got any suggestions on the VA rating? What I do know is the excitation is based on 125Vdc and the 'expired' regulator was rated 5A 50/60Hz. Are we talking a 750VA 480:120V transformer?
2) We need to provide an (overvoltage) circuit breaker that interrupts the 120Vac of the aforementioned transformer to drop the excitation in the event of an unexpected overvoltage occurrence. This is a shunt-trip breaker that needs to be electrically tripped by the Vreg. I have no idea what brands or current rating I need. Got any suggestions?
3) I believe you need to keep the excitation leads straight since they're DC. Is this true and if so is there any standard I can expect to see in the marking to know which wire is [ [!]+[/!] ]? Red? #1?
Thanks for any help.
Keith Cress
kcress -
Keep in mind I have NO spec plate on the unit what-so-ever. The V12 turbo'd engine generator is 480VAC delta supplying a handful of rail cars in a seasonal (this season) application. It is not paralleled.
The existing regulator is a Basler Electric APR125-5 (giant potted brick) which is no longer available.
The replacement is a VR902 made by who-knows. ESI??
We're supposed to include a power transformer between two phases that supplies the power to the regulator for the regulator to use for the generator's excitation.
1) How do I size this thing? Since I have no measured or nameplate info on the generator's excitation range, have you got any suggestions on the VA rating? What I do know is the excitation is based on 125Vdc and the 'expired' regulator was rated 5A 50/60Hz. Are we talking a 750VA 480:120V transformer?
2) We need to provide an (overvoltage) circuit breaker that interrupts the 120Vac of the aforementioned transformer to drop the excitation in the event of an unexpected overvoltage occurrence. This is a shunt-trip breaker that needs to be electrically tripped by the Vreg. I have no idea what brands or current rating I need. Got any suggestions?
3) I believe you need to keep the excitation leads straight since they're DC. Is this true and if so is there any standard I can expect to see in the marking to know which wire is [ [!]+[/!] ]? Red? #1?
Thanks for any help.
Keith Cress