Hello all. I have a 25 h.p. rotary phase converter that was purchased new about 3 years ago. Since then, we've burned up the idler motor twice. Both were new Reliance induction motors. The phase converter is of the transformerless variety.
I'd like to know, is there anyway one could wire up a 3 phase motor to 240V, single phase, using only capacitors, that could cause a voltage spike sufficient to burn out the stator winding? I don't think it's inrush current burning up the motors and that's probably the obvious suspect. I want to consider the voltage as the cause.
The converter is never started under load, electrical or mechanical. Once running, the load is balanced within 5%. All machines operate without one iota of problems. Most are manual machine tools under 6 hp. One machine is a CNC mill with a 10 hp spindle. The mill is loaded with built-in electronics, onboard computer, etc. The mill does have a vector drive and it's been suggested that harmonics could be creating a problem. While I'm not disputing that, I am reluctant to commit to it as the cause. In fact, I believe this problem is happening at start up. Both times the motor burned out, was shortly after startup. The last time, I hadn't even turned on a load.
Here's the part that bothers me. A varistor circuit protects the CNC mill. They've never faulted, except for one time. I had inadvertently thrown the mill knife switch to on before turning on the RPC. When the mill didn't power up, I quickly realized my error and switched on the RPC, forgetting to turn the mill off beforehand. The varistors blew immediately. Since the varistors can only blow during an over-voltage condition, I'm wondering what could have caused it? There IS a 3 phase buck boost transformer in the mill. I don't know if that matters.
I did discover some wiring errors in the RPC control box, but I'll withhold that information for now. First, I want to see what you think. Is there anyway to create a momentary high voltage with just a motor and some caps? Sufficient to burn up the insulation on 18 gage windings? Assume nothing wrong with the wiring from panel to RPC.
I'd like to know, is there anyway one could wire up a 3 phase motor to 240V, single phase, using only capacitors, that could cause a voltage spike sufficient to burn out the stator winding? I don't think it's inrush current burning up the motors and that's probably the obvious suspect. I want to consider the voltage as the cause.
The converter is never started under load, electrical or mechanical. Once running, the load is balanced within 5%. All machines operate without one iota of problems. Most are manual machine tools under 6 hp. One machine is a CNC mill with a 10 hp spindle. The mill is loaded with built-in electronics, onboard computer, etc. The mill does have a vector drive and it's been suggested that harmonics could be creating a problem. While I'm not disputing that, I am reluctant to commit to it as the cause. In fact, I believe this problem is happening at start up. Both times the motor burned out, was shortly after startup. The last time, I hadn't even turned on a load.
Here's the part that bothers me. A varistor circuit protects the CNC mill. They've never faulted, except for one time. I had inadvertently thrown the mill knife switch to on before turning on the RPC. When the mill didn't power up, I quickly realized my error and switched on the RPC, forgetting to turn the mill off beforehand. The varistors blew immediately. Since the varistors can only blow during an over-voltage condition, I'm wondering what could have caused it? There IS a 3 phase buck boost transformer in the mill. I don't know if that matters.
I did discover some wiring errors in the RPC control box, but I'll withhold that information for now. First, I want to see what you think. Is there anyway to create a momentary high voltage with just a motor and some caps? Sufficient to burn up the insulation on 18 gage windings? Assume nothing wrong with the wiring from panel to RPC.