I went acrros several generator data sheets.
A standard capability curve is "voltage vs. frequency operating limits".
I do understand there is a min. and a max. values for both frequency and voltage.
I also understand there is 2 limits zones : one for permanent operation whithin the second one ( operation bounded in time).
let's gives some figures :
first zone :
Freq. +- 2%
U +- 5%
second zone ( allowable for less than 1 hour) :
Freq. + 3% - 5%
U +- 8%
> first issue is than generator is "more sensible" to overfrequency rather than underfrequency. ( Gen. is able to whistand a 5% underfreq. but not a 5% overfrequency)
> Main issue is that gen. may handle at the same time max (resp. min) U allowable value and max ( resp. min) f allowable value.
BUT the same gen. shall not operate with at the time max( resp. min) U allowable value and min( resp. max) f allowable value.
Any clues to explain such limits ?
A standard capability curve is "voltage vs. frequency operating limits".
I do understand there is a min. and a max. values for both frequency and voltage.
I also understand there is 2 limits zones : one for permanent operation whithin the second one ( operation bounded in time).
let's gives some figures :
first zone :
Freq. +- 2%
U +- 5%
second zone ( allowable for less than 1 hour) :
Freq. + 3% - 5%
U +- 8%
> first issue is than generator is "more sensible" to overfrequency rather than underfrequency. ( Gen. is able to whistand a 5% underfreq. but not a 5% overfrequency)
> Main issue is that gen. may handle at the same time max (resp. min) U allowable value and max ( resp. min) f allowable value.
BUT the same gen. shall not operate with at the time max( resp. min) U allowable value and min( resp. max) f allowable value.
Any clues to explain such limits ?