Hi folks,
Would like some comments on installing a VRLA (valve regulated lead acid) battery in an explosion proof enclosure that will be installed outdoors. The area is Class I Div 2 Group D.
Originally planned to install in a louvered battery box.
Client questioned classification of battery, specifically whether the battery would emit an arc and possibly ignite a flammable atmosphere if the battery exploded or malfunctioned due to perhaps a runaway charger (which has protection). No battery manufacturer would say "yes" or "no", so the explosion proof enclosure came into the plan. If there is an arc emitted during a battery explosion, it should not ignite the atmosphere around the enclosure.
BTW: We are including signage to open a disconnect prior to connecting and/or disconnecting wires to battery to prevent arcing.
What about hydrogen inside the enclosure?
Max allowable hydrogen in enclosure is 1% by volume (25% of LEL which is 4% for Hydrogen)
The specified battery has an almost negligible hydrogen evolution since it has a recombination process for the hydrogen and oxygen.
The enclosure will have a breather and drain (suited for C1D2) which is capable of venting air at 0.05 ft^3/min.
The hydrogen evolution from the battery is much lower at 0.0000351 ft^3/min.
Enclosure volume is 1 ft^3
Free space in enclosure (after subtracting battery volume) is 0.67 ft^3
Some of the questions in my head:
1) Can I assume there will always be a constant natural convection flow to vent the hydrogen?
2) Will the hydrogen concentration in the enclosure be below 1%?
3) Does venting the hydrogen affect the classification outside the enclosure (is it now C1D1, Group B?
I'd like to get your comments on this and see if you folks have been down this road already.
Sincere thanks!!!
Would like some comments on installing a VRLA (valve regulated lead acid) battery in an explosion proof enclosure that will be installed outdoors. The area is Class I Div 2 Group D.
Originally planned to install in a louvered battery box.
Client questioned classification of battery, specifically whether the battery would emit an arc and possibly ignite a flammable atmosphere if the battery exploded or malfunctioned due to perhaps a runaway charger (which has protection). No battery manufacturer would say "yes" or "no", so the explosion proof enclosure came into the plan. If there is an arc emitted during a battery explosion, it should not ignite the atmosphere around the enclosure.
BTW: We are including signage to open a disconnect prior to connecting and/or disconnecting wires to battery to prevent arcing.
What about hydrogen inside the enclosure?
Max allowable hydrogen in enclosure is 1% by volume (25% of LEL which is 4% for Hydrogen)
The specified battery has an almost negligible hydrogen evolution since it has a recombination process for the hydrogen and oxygen.
The enclosure will have a breather and drain (suited for C1D2) which is capable of venting air at 0.05 ft^3/min.
The hydrogen evolution from the battery is much lower at 0.0000351 ft^3/min.
Enclosure volume is 1 ft^3
Free space in enclosure (after subtracting battery volume) is 0.67 ft^3
Some of the questions in my head:
1) Can I assume there will always be a constant natural convection flow to vent the hydrogen?
2) Will the hydrogen concentration in the enclosure be below 1%?
3) Does venting the hydrogen affect the classification outside the enclosure (is it now C1D1, Group B?
I'd like to get your comments on this and see if you folks have been down this road already.