MECE23
Mechanical
- Oct 7, 2013
- 2
Hello All:
I have a control cabin in a NEC 505 Class 1 Zone 2 Area.
The cabin is Type Z purged per NFPA 496
Upon loss of purge i can still run equipment, i just have to monitor the environment.
If i lose purge i am likely now on UPS battery power.
The question is, if the VRLA's are inside the cabin, and i have no airexhanges to keep below LEL from the VRLA hydrogen off gassing, is this going to be a concern and will it harm the personnel inside? How do you mitigate this? Stick the batteries outside the cabin?
The batteries say they are classified for the hazardous area, but i dont see how that can be so if they themselves emit gas.
Maybe they are only classified if they are also in a purged environment?
What happens when i lose purge AND gas alarms trigger? Everything shuts down except my Zone 1 F&G panel and alarms and my batteries that are contributing to the cause?
-Sorry, I'm a Mech eng in an electrical world at the moment
I have a control cabin in a NEC 505 Class 1 Zone 2 Area.
The cabin is Type Z purged per NFPA 496
Upon loss of purge i can still run equipment, i just have to monitor the environment.
If i lose purge i am likely now on UPS battery power.
The question is, if the VRLA's are inside the cabin, and i have no airexhanges to keep below LEL from the VRLA hydrogen off gassing, is this going to be a concern and will it harm the personnel inside? How do you mitigate this? Stick the batteries outside the cabin?
The batteries say they are classified for the hazardous area, but i dont see how that can be so if they themselves emit gas.
Maybe they are only classified if they are also in a purged environment?
What happens when i lose purge AND gas alarms trigger? Everything shuts down except my Zone 1 F&G panel and alarms and my batteries that are contributing to the cause?
-Sorry, I'm a Mech eng in an electrical world at the moment