Hi Guys
I have searched heaps of threads here, and on mikeholt.com about using MCCBs on VSDs/VFDs, even though the manufacturer recommends semiconductor fuses. I Haven't really found anything relating to my question though, here goes...
We have several 400V drives (largest being 315kW) with short circuit rating = 65kA "with the specified fuses". These fuses are gR semiconductor fuses which are current limiting (Siemens 3NE1436-2).
The customer has specified MCCBs on the line side of these drives. The MCCB is current limiting, but not as good as the fuse (Schneider NS400L).
The big issue in this application is that the prospective fault current at the location of these drives is 65kA... the same as the SCCR of the VSD with line side fuses. So without fuses, the fault withstand of the drive would definitely be less than the prospective fault current in this part of the plant.
Surely in this case it would be essential to use the recommended fuses... Thoughts?
Thanks
I have searched heaps of threads here, and on mikeholt.com about using MCCBs on VSDs/VFDs, even though the manufacturer recommends semiconductor fuses. I Haven't really found anything relating to my question though, here goes...
We have several 400V drives (largest being 315kW) with short circuit rating = 65kA "with the specified fuses". These fuses are gR semiconductor fuses which are current limiting (Siemens 3NE1436-2).
The customer has specified MCCBs on the line side of these drives. The MCCB is current limiting, but not as good as the fuse (Schneider NS400L).
The big issue in this application is that the prospective fault current at the location of these drives is 65kA... the same as the SCCR of the VSD with line side fuses. So without fuses, the fault withstand of the drive would definitely be less than the prospective fault current in this part of the plant.
Surely in this case it would be essential to use the recommended fuses... Thoughts?
Thanks