raar
Electrical
- Aug 17, 2010
- 11
Have a grinder machine with an approximately 1HP motor with a Mitsubishi Model FR-D720-1.5K drive. Per the machine manual (English), the product requires 230 VAC, 3-Phase, 3-wire, 60Hz and appears to be originally designed to IEC standards, but also sold in North America. We've already had a 3rd party FEB inspect for NFPA 79 compliance and in-process of determining related corrective actions.
Our building distribution is 480 VAC, 3-Phase, 3-wire, 60 HZ, and desire to install an equipment / isolation transformer for this machine, with no intention on providing that voltage for other loads using an existing 30A disconnect, to transformer (to be selected and installed), then to another disconnect (to be installed) for the machine with appropriate protection via disconnect fusing. The cabling distances are approximately ~20 or less feet from existing disconnect to proposed mounting location for transformer and about 20-40 feet to the machine from there. The drive is installed on the machine and has 20 feet or less cable run to its motor.
I desire to provide a grounded separately derived system for this machine, so believe my options are a either appropriately sized delta-wye or delta-delta with a high leg delta in order to minimize the number of items for our installers. Finding an off the shelf, listed, 3-phase, 60Hz, 480:240/120 VAC (delta-delta) or 480:240Y VAC (delta-wye), 7.5KVA, K-Factor (4, or 13) transformer, 115C rise hasn't yielded many results. Need a relatively quick solution (part arrival within 2-3 weeks from order), so believe I have to find available off the shelf. For energy reasons I'd prefer not to install a substantially larger transformer if possible, but am open to suggestions.
Yesterday I did find this transformer that is defined as a Drive Isolation Transformer, DTGA72S, but doesn't seem to specify a K-Rating. When I view the image for that transformer it appears to just list "General Purpose". Although described as 460:230 VAC, it has a 5% above and below tap on primary, so I believe from a voltage standpoint it could work. Somewhat recently we ran a couple hour power test at a busy time of day and voltages stayed at 480 VAC with little deviation (+/- 1 VAC).
Would you consider this transformer for this application? If not, why? Any other suggestions?
Thank you for any assistance related to this.
Attachment links: Transformer Catalog - Drive Spec Sheet
Our building distribution is 480 VAC, 3-Phase, 3-wire, 60 HZ, and desire to install an equipment / isolation transformer for this machine, with no intention on providing that voltage for other loads using an existing 30A disconnect, to transformer (to be selected and installed), then to another disconnect (to be installed) for the machine with appropriate protection via disconnect fusing. The cabling distances are approximately ~20 or less feet from existing disconnect to proposed mounting location for transformer and about 20-40 feet to the machine from there. The drive is installed on the machine and has 20 feet or less cable run to its motor.
I desire to provide a grounded separately derived system for this machine, so believe my options are a either appropriately sized delta-wye or delta-delta with a high leg delta in order to minimize the number of items for our installers. Finding an off the shelf, listed, 3-phase, 60Hz, 480:240/120 VAC (delta-delta) or 480:240Y VAC (delta-wye), 7.5KVA, K-Factor (4, or 13) transformer, 115C rise hasn't yielded many results. Need a relatively quick solution (part arrival within 2-3 weeks from order), so believe I have to find available off the shelf. For energy reasons I'd prefer not to install a substantially larger transformer if possible, but am open to suggestions.
Yesterday I did find this transformer that is defined as a Drive Isolation Transformer, DTGA72S, but doesn't seem to specify a K-Rating. When I view the image for that transformer it appears to just list "General Purpose". Although described as 460:230 VAC, it has a 5% above and below tap on primary, so I believe from a voltage standpoint it could work. Somewhat recently we ran a couple hour power test at a busy time of day and voltages stayed at 480 VAC with little deviation (+/- 1 VAC).
Would you consider this transformer for this application? If not, why? Any other suggestions?
Thank you for any assistance related to this.
Attachment links: Transformer Catalog - Drive Spec Sheet