I recently had the privilege of doing a project for MD (2015 IBC). One of my deviations was that I must list both Vult and Vasd on the drawings. I did it to please the state, but I don't know why I had to do it. They referenced section 1609.3.1 as the requirement for listing both, but I still disagree. I was told that if I think there is a conflict with the IBC that I should contact ICC for an opinion, but I am not a member and there is no conflict in my interpretation. Also, opinions are not official positions of ICC and the state could still ignore it. I wrote them the following.
A Vasd of 93 mph with risk category I or IV are both equal to a Vult of 120 mph? Vasd has to be limited to risk category II structures (importance factor 1) anyway (my structure is overdesigned as RC=IV) or the conversion falls apart:
Juston Fluckey, SE, PE, AWS CWI
Engineering Consultant
Juston said:Please follow the progression through the code below.
1.) 1603.1.4(1): Ultimate design wind speed, Vult, (3-second gust), miles per hour (km/hr) and nominal design wind speed, Vasd, as determined in accordance with Section 1609.3.1.
2.) Go to 1609.3.1 to find out how to be "in accordance"
3.) 1609.3.1: When required, the ultimate design wind speeds of Figures 1609.3(1), 1609.3(2), and 1609.3(3) shall be converted to nominal design wind speeds, Vasd, using Table 1609.3.1 or Equation 16-33.
4.) When is it required? In this very same section (1609.3.1) Vasd is defined as "Nominal design wind speed applicable to methods specified in Exceptions 4 and 5 of Section 1609.1.1.
5.) Go to 1609.1.1 to find out Exceptions 4 and 5 are:
* Designs using NAAMM FP 1001* Designs using TIA-222 for antenna-supporting structures and antennas, provided the horizontal extent of Topographic Category 2 escarpments in Section 2.6.6.2 of TIA-222 shall be 16 times the height of the escarpment.6.) Notice ASCE 7 is not part of exceptions 4 and 5 so there is no need to list Vasd on construction documents.
I have provided an actual argument above, but my logical argument: Vasd provides no relevant information to the building department unless it is to cross reference wind speeds used in the standards of Exceptions 4 and 5 (NAAMM FP 1001 and TIA-222) which relate to flagpoles and antenna structures. So why require it for all structures? I don't want to ruffle any feathers, but at the same time I don't like having to do something that isn't necessary.
A Vasd of 93 mph with risk category I or IV are both equal to a Vult of 120 mph? Vasd has to be limited to risk category II structures (importance factor 1) anyway (my structure is overdesigned as RC=IV) or the conversion falls apart: