Wall and Column Kickers - Why (Pros and Cons) 2
Eng9876
DE
This is a new thread based on this one that was closed. I felt that the answers given were not complete
Kickers aren't being used so much in construction today, a lot of new construction engineers are learning methods that can be more risky whereas taking a little extra time and setting a template (kicker) against each column/wall can pay back in dividends when saving re-work.
I was recently involved in a project with over 300 columns (using mainly unskilled labour in the middle east), with not one single cover or steel/column alignment issue, how many people can say that?
Why?... we used kickers.
What are kickers?:
A kicker is a small concrete plinth 50-150mm (2"-6") in height placed around a column base in order for you to quickly start your next stage column pour - it sets out the alignment pre-pour rather than post-pour (because if you need to move things, you can do it there and then). It is usually cast with the floor, pad or raft foundation. Construction can be fiddly/slows concreting for the first stage foundation slightly, but lost time is usually made up in time at the column/wall erection stage (if you have crews that know what they are doing).
Having a kicker you can physically see what's not right both in terms of cover and by looking along the kicker bases gives a quick visual indication of what needs to be moved. Obviously your surveyor would set-up a local grid to set these things out. It is easier to look along a straight edge of columns than it is a long string line with wavy 32mm reinforcement starter bars (which are usually placed where they can due to base steel configuration).
The reason why we have column and wall kickers are as follows:
From Checking Engineers Perspective:
For Having a Kicker - Pro's:
1, You can see any column or wall alignment issues immediately, fix any grid problems straight away(Once the concrete is cast and steel alignment problems exist, you don't have to cut the steel, just move it before you pour).
2. Makes the next stage construction (columns and walls) much faster as you only have to butt up your formwork against the kicker (alignment is already done).
3. Gives additional level(concrete elevation) guides as well as screed rails therefore providing better elevation control.
4. Reduces the amount of joints in the concrete. (you only have one joint where a second stage kicker would give you two. - NOT GOOD!)
For having a kicker - Cons:
1. Slower (INITIAL) stage pouring, but less risky. Slightly more fiddly initial construction for carpenters - this is however made up for at the next stage of construction.
2. Has to be done right - a finishing team must know what they are doing, if they mess up, concrete re-work will slow progress down. (use experienced concrete finishers - which you would do anyway).
From the contractors Perspective:
For not having a kicker - Pros:
1. Faster (INITIAL)construction, but risky. (however, many contractors cast a kicker at the second stage but this increases the number of joints in the concrete WHICH IS NOT GOOD). you will lose this time easily with all the re-work.
For not having a Kicker - Cons:
1. Any mistakes in the steel reinforcement could prove costly, whole gridlines in the wrong location may involve structural engineering to fix.
2. Cover issues may need re-work.
3. Increases the amount of joints in the concrete.
4. Once the concrete is poured and has set, mistakes require costly rework and potential structural engineering.
It is always best to have a kicker, you can see any alignment or cover issues straight away and fix them. Any time lost through making kickers is always made up at the next stage. You simply butt up your formwork against the kicker and plumb down for verticality. (don't forget your top column alignment.)
Not having a kicker is risky, best to take your time and get it right. Don't use inexperienced crews for concrete finishing, this is an added risk (and re-work) factor you don't need.
I'll bite. Why would you not want to do that on your jobs?
They actually make structures work a lot easier on the design side because you're forced by the tunnel system to have walls at a maximum of about 15' on center. Slab deflection is practically nothing with relatively little reinforcement for spans that small, wall stresses are extremely low because you've got so many of them. Can get by with relatively minimal reinforcement for low- and mid-rise buildings. Not sure what there is not to like from a structural standpoint.
Goes up extremely quickly as well.
I think I know why hokie66 doesn't want it on his jobs. Pouring walls and slabs together creates gaps in the walls due to concrete settlement while curing.
BA
When you cast the wall and slab together, the top of the wall is subject to plastic settlement cracking. The form supports the slab, while the concrete in the wall continues to settle a bit. Those plastic cracks can be closed by revibration, but when speed is the overriding principle, I would think the revibration may be overlooked. This is the reason you don't cast columns with the supported floor.
Understand what you're getting at, but this formwork system has been in use around the world for over thirty years now (Concrete Construction Article from 1982 on vibration of concrete in tunnel forms). To my knowledge, have never seen any issues reported with monolithic pours of walls/slabs in tunnel forms. Keep in mind the pour occurs at the exact same time, this isn't pour your walls in the morning and slabs in the afternoon. Usually the wall/slab mix is the same and poured during the same continuous pour. Proper consolidation is of course important as it is with any other job. Fortunately tunnel forms are rather specialized so the contractors who use them tend to know them well and know what they need to do to produce a quality building. All of our tunnel form jobs have been with the same contractor because they're the only ones in the area with the forms to do it. Speed is always a driving factor with every job. With tunnel forms what we've seen is the formwork provides the speed. There's not as much pressure on the contractors to skimp on the consolidation, inspection, and QC because they're already moving much quicker than normal with the forms.
But let's assume that we do get settlement cracks at the top of the wall, right underneath slab soffit. Would tend to think these would be horizontal cracks. Once you remove the formwork wouldn't the cracks close up on their own as the weight of the slab goes in to the wall? At that point would it really behave any different than the construction joint (really just an intentional crack) you'd get between slab and wall anyways?
@hokie: a few weeks ago, I read an excellent AU document on plastic settlement cracking that you referred me to. Based on my read of that document, the expected problem here would be slab cracking adjacent to the wall rather than gap formation at the slab/wall joint. Can you confirm that? Ditto for you BA if you have personal experience with this.
@MrHershy: with these buildings, what is the lateral system perpendicular to the tunnels?
Tunnels go in both direction. Just turn them 90 degrees and you've got shear walls in both directions.
Another example from Google image search, not mine:
KootK,
The plastic settlement cracking can be either horizontal at the top of the wall, or vertical in the slab adjacent to the wall, both due to continued settlement of the wall concrete after placement and vibrating, while the slab concrete remains supported on the forms. As in all plastic cracks, if you get to them quick enough, you can close them by revibration.
Mr.Hershey,
No, I wouldn't consider a horizontal crack which closes when the forms are removed to be the same as a normal construction joint, which closes in the plastic state of the slab. Pouring "the walls in the morning and slabs in the afternoon" is better practice, but I suppose that is not how this system is intended to be used.
KootK,
I have never witnessed the problem because I have never permitted slabs to be poured monolithically with walls or columns. Our code recognizes the problem by increasing required development length of horizontal reinforcement by 30% when it is placed such that more than 300mm (12") of fresh concrete is cast below the reinforcement.
BA
BA,
I think that requirement is generally for top steel in deeper beams, and is indeed another example of the adverse affects of plastic settlement. Another example is the reflective cracking over top bars in deep elements like spread footings with top steel.
