Greetings All,
I'm working on a handrail project that has a very typical situation: Wall handrail with brackets and sleeve anchors into clay brick. Surely there are a million lineal feet of these in service.
Attached is how I would approach this problem. The rail is subjected to either 200 lb or 50 plf. If I sum moments around the bottom of the bracket, I get an anchor tensile force of 816 lb. This value far exceeds the 3/8 in. sleeve anchor allowable strength shown in the Hilti Table 6.
I'm trying to figure out how people make these "calc out."
Am I missing something big here? Are the 200 lb and 50 plf excessive? Is there some way to justify not considering the eccentricity like I did? etc.?
Is the 4.0 factor of safety (Hilti table footnote) required? In this case, the FS would be about 1.8. I could not find a code provision requiring 4.0, but maybe one exists. Is there something stopping me from saying 1.8 is good enough?
Something else?
Any advice would be appreciated!
I'm working on a handrail project that has a very typical situation: Wall handrail with brackets and sleeve anchors into clay brick. Surely there are a million lineal feet of these in service.
Attached is how I would approach this problem. The rail is subjected to either 200 lb or 50 plf. If I sum moments around the bottom of the bracket, I get an anchor tensile force of 816 lb. This value far exceeds the 3/8 in. sleeve anchor allowable strength shown in the Hilti Table 6.
I'm trying to figure out how people make these "calc out."
Am I missing something big here? Are the 200 lb and 50 plf excessive? Is there some way to justify not considering the eccentricity like I did? etc.?
Is the 4.0 factor of safety (Hilti table footnote) required? In this case, the FS would be about 1.8. I could not find a code provision requiring 4.0, but maybe one exists. Is there something stopping me from saying 1.8 is good enough?
Something else?
Any advice would be appreciated!