mustang17
Electrical
- Sep 4, 2007
- 5
I have a pumping application with three 5 HP motors on full voltage starters. Motors and pumps are floor mounted on housekeeping pads in a class 1, div 1 area. Motors are explosion proof.
Due to some problems in the process the floor has required frequent hosing and during a recent wash-down activity an operator with wet leather boots, and wet hands felt tingling coming up both legs from the floor. We checked for proper equipment grounding in the building and made sure all metal and plumbing including floor drains was at the same potential. This checked out good.
Even though the operator claims that he did not hit the motor directly with the stream of water coming out of the hose I have a difficult time understanding how they might have felt current. Explosion proof motors although not submergence proof are very tight. It would seem that you would have to stand there with the water directly on the motor for minutes and even perhaps hours to get water to leak into the motor and perhaps be able to pass current through your body to ground.
This also led me to question the application. We have no choice but to use explosion proof motors due to the hazardous area but I was not able to find an exp rated motor that was also wash-down rated. Anyone know if such a motor exists?
Finally I do not know all OSHA standard and who possibly could but does anyone know what would be a recommended operational practice with regards to wash-down activities using an exp motor. Should they be locking it out. What about with a wash-down rated motor. Would it then be acceptable to keep the wash-down rated motors running while wash-down activities proceeded?
Thanks, Ed
Due to some problems in the process the floor has required frequent hosing and during a recent wash-down activity an operator with wet leather boots, and wet hands felt tingling coming up both legs from the floor. We checked for proper equipment grounding in the building and made sure all metal and plumbing including floor drains was at the same potential. This checked out good.
Even though the operator claims that he did not hit the motor directly with the stream of water coming out of the hose I have a difficult time understanding how they might have felt current. Explosion proof motors although not submergence proof are very tight. It would seem that you would have to stand there with the water directly on the motor for minutes and even perhaps hours to get water to leak into the motor and perhaps be able to pass current through your body to ground.
This also led me to question the application. We have no choice but to use explosion proof motors due to the hazardous area but I was not able to find an exp rated motor that was also wash-down rated. Anyone know if such a motor exists?
Finally I do not know all OSHA standard and who possibly could but does anyone know what would be a recommended operational practice with regards to wash-down activities using an exp motor. Should they be locking it out. What about with a wash-down rated motor. Would it then be acceptable to keep the wash-down rated motors running while wash-down activities proceeded?
Thanks, Ed