peakpilgrim - Large clarifiers, identical to wastewater clarifiers, are used as part of the flue gas desulfurization (FGD) system at certain coal fired electric generating stations. I agree with
bridgebuster, concrete is placed from low to high. For a [highlight #8AE234]qualified[/highlight] Contractor, accurately placing properly vibrated (pokered) concrete on a 6:1 slope is not difficult. Concrete slump and the concrete placement rate have to be controlled. The Engineer needs to stay out of this "means & methods" aspect of the project. The Contractor has to have the authority to quickly alter his in-progress field operations depending of variables such as weather, concrete delivery, and manpower.
Concerning your paragraph #2... I believe you need to review how a clarifier works. There are radial rakes just above the bottom that rotate slowly to gather sludge and direct it to the center (underflow). The concrete bottom has to be constructed to fairly tight tolerances (in the radial direction in particular), or the equipment won't work. I suggest you forget about detailing 20+ construction joints and approximations of the required slope.
As a former Owner's Representative, I would reject that (Engineer's) concept based on its needless complexity alone.
As a former Bridge / Heavy Construction Contractor, the bid I would submit (to perform work to that detail) would be so high that that the Owner would reject the bid based on excessive price. Concrete volume of 385 cubic meters (35 meters, diameter, 0.4 meters thick) is not enough for a Contractor to economically justify very many concrete placements.
I suggest your drawing / specification show the slab, including appropriate construction tolerances, without any construction joints. A prominent note states that a Bidder should summit proposed construction joints, if any, with the bid. This submittal will be evaluated by the Engineer during the bid review process.