Wastewater Forcemain Thrust Blocks

Status
Not open for further replies.

zahid106

Civil/Environmental
Nov 3, 2000
16
Do we need thrust block restraints on HDPE sewage forcemain bends that are fusion welded?
 
Replies continue below

Recommended for you

I agree with bimr. Thrust restraint in piping keeps it from separating at joints where thrust exists (eg. bends, tees, dead ends). If all connections are fusion bonded, then no separation can occur and there is no need for thrust restraint.
 
I imagine that there are no branches on this force main? I did a fire main in PE and had to but thrust blocks on the T's to avoid them possibly breaking off and also had to put some thrusts to prevent it lifting so if you have some vertical bends you may have to put thrusts on them.

suppose it all depends on what pressures and fluctuations you expect
 