Hi,
I am specifying my first water booster pump, and would like to hear how you other engineers determine whether a booster pump is needed and the amount of pressure boost that is needed.
My calculations are as follows:
Water flow test
Pressure losses:
Pressure Required at the fixture
Required Pressure: 91.5 psi @ 200 gpm
Available Pressure: 57 psi @ 200 gpm
Pressure Boost: (91.5psi-57psi) = 34.5 psi + 5psi booster loss = 40 psi
A 40 psi, 200 gpm booster pump set is required.
Happy Thanksgiving!,
Thanks!
I am specifying my first water booster pump, and would like to hear how you other engineers determine whether a booster pump is needed and the amount of pressure boost that is needed.
My calculations are as follows:
Water flow test
static pressure: 58psi
residual pressure: 54psi
test flow: 1800 gpm
available pressure at building peak flow: 57 psi @ 200 gpm
Pressure losses:
10 psi - 4" Reduced Pressure Zone Backflow Preventer - Watts LF-909 - 200 gpm
8 psi - 3" compound meter - AWWA tables - 200 gpm
17 psi - 39ft static head (4th floor)
20 psi - 400 ft of pipe @ 4psi/100ft + fittings + accessories
5 psi - Leonard Valve Master Mixing Valve TM-2020B-3PS-L @ 200 gpm
1.5 psi - tap & 50ft 4inch water service pipe
-----------------61.5 psi
Pressure Required at the fixture
20 psi - pressure balanced shower valve (per IPC 2012)
10 psi - ASSE 1070 point of use temperature limiting valve (per local code)
-----------------30 psi
Required Pressure: 91.5 psi @ 200 gpm
Available Pressure: 57 psi @ 200 gpm
Pressure Boost: (91.5psi-57psi) = 34.5 psi + 5psi booster loss = 40 psi
A 40 psi, 200 gpm booster pump set is required.
Happy Thanksgiving!,
Thanks!