I am design a water chiller for 1320 gallon tank. The ambient will reach to 50c (122F) on summer. The Required water temperature 4c has to be reached within 70 minutes.1320 divided by 70=18 gpm. I assume if ambient is 122F then the water will be 104F.so I calculate the chiller capacity GPM*DELTA T/24(20*65/24=54 ton. Should I consider any other things? Thanks for the advice.