I have looked on other threads. I have looked at technical documents. I have looked at on line calculators.
I am missing something.
There seems to be two different ways to calculate the pressure and/or force exerted when flow is stopped by a quick acting valve, i.e. water hammer.
One way per thread124-18869 indicates h(wh)=a*DV/gc where a is the velocity of wave propagation, D is the inside pipe diameter, V is the change in velocity of the fluid, and gc is the grav. constant.
Then there is the other approach/method found in several locations including engineering toolbox for water hammer which states P=0.07VL/T where V is the velocity, L is the pipe length, t is the valve closing time.
I am assuming h(wh) and 0.07VL/T are analogous in that they represent the surge in pressure on the system caused by the velocity drop, but i do not see how since they use different system variables
Assume
a = 4,000 ft/s
D = 0.5 in
V = 10 ft/s
gc = 32.2
L = 20 ft
T = 0.1 sec
Unless I am missing something, the first equation lacks the density of water (62.4 lb/cf) to make the units work and adding conversions from feet to inches so
lb/in^2 = 10*4000*0.5*62.4 / 32.2*1728
= 22.4
When I use the second equation, which the units do not get to pressure,
lb/in^2 = 0.07*10*20/0.1
= 140
What am i missing?
I am missing something.
There seems to be two different ways to calculate the pressure and/or force exerted when flow is stopped by a quick acting valve, i.e. water hammer.
One way per thread124-18869 indicates h(wh)=a*DV/gc where a is the velocity of wave propagation, D is the inside pipe diameter, V is the change in velocity of the fluid, and gc is the grav. constant.
Then there is the other approach/method found in several locations including engineering toolbox for water hammer which states P=0.07VL/T where V is the velocity, L is the pipe length, t is the valve closing time.
I am assuming h(wh) and 0.07VL/T are analogous in that they represent the surge in pressure on the system caused by the velocity drop, but i do not see how since they use different system variables
Assume
a = 4,000 ft/s
D = 0.5 in
V = 10 ft/s
gc = 32.2
L = 20 ft
T = 0.1 sec
Unless I am missing something, the first equation lacks the density of water (62.4 lb/cf) to make the units work and adding conversions from feet to inches so
lb/in^2 = 10*4000*0.5*62.4 / 32.2*1728
= 22.4
When I use the second equation, which the units do not get to pressure,
lb/in^2 = 0.07*10*20/0.1
= 140
What am i missing?