Water main design for small subdivision 1
sketchhwyman
I am trying to model the water distribution network for a small subdivision and check fire flow pressures, etc. For the mains that we will be tying into we have the following information at hydrant locations: static pressure, residual pressure, calculated flow, and measured flow at 20 psi. How do I take that information and use as input it in either Hardy Cross or EPANET to model my system?
You can use the data from the hydrant flow test to create a pump curve. Then you set a reservoir or storage facility at the site of the fire hydrant and place the pump you have created next to the reservoir and connect it with a large pipe to reduce head losses. From the hydrant you can run a connection to your tie-in point. You can find the formula to convert the pressure & flow data to a pump curve in AWWA M-17 or in the Haestad Book "Advanced Water Distribution Modeling and Management." I believe you can still read it online. You might also want to get a copy of AWWA M32 "Computer Modeling of Water Distribution Systems". Be aware that the hydrant flow test data represents a system snapshot only and should be balanced against data on what pumps were running, system demands at the time, etc.
Good luck