The surge anticipator valves (surge relief) are indeed high maintenance valves due to the multiple pilots and complex piping. A surge anticipator valve normally will include: 1- high pressure pilot, 1- low pressure pilot, 1- flow limiter (to restrict amount of main valve opening), 1- control pilot valve, 1- strainer/needle valve assy., opening and closing speed controls, and numerous other cocks, copper tubing, and fittings. The initial adjustment and maintenance of the adjustment is critical for proper response and operation of the valve. A pressure relief valve, on the other hand, will generally only have a high pressure pilot, speed controls, and control pilot for pilot control over the main valve. Adjustment is much simpler to initially perform and maintain than a surge valve. As I mentioned in my previous post, a surge valve in the wrong application is often worse than using no valve at all. Make sure that your system has adequate supply and pressure to reclose the valve after the initial low pressure wave, otherwise the valve might remain open and never close because the pressure cannot recover enough to reset the pilot system. Hope this helps, epbpe.