I am sorry for this rookie question, but I can not find where the norm NFPA stablishes how to calculate the volume that the water tank for private fire protection should have.

I only found the "standard net capacity sizes" on the NFPA22, but I didn´t find any tips on how to determine the size.

Can anyone please help me to find it?
 
Replies continue below

Recommended for you

NFPA 13 is where the details are located.

Sprinkler demand + inside hose streams + outside hydrants times the duration based on the occupancy. Light 30 min, Ordinary Haz 1 & 2 60 mins, Extra Haz 1 & 2 120 mins. Warehouses 120 mins, ESFR 60 mins.

Example

Light hazard .10/1500= 150 gpm plus 100 gpm hose = 250 gpm times 30 mins = 7,500 gallons. If no inside hose then deduct 100 gpm.

Hope this helps.

****************************************