Please see attached drawings for information.
The system was designed to run 2, 3 or 4 pumps based on pump suction pond level and water user requirement. The system must keep certain pressure at the branch to send water to user 1.
The problem with figure 1 is that the section of the piping (sloped) downstream of the vacuum breaker is equivalent to a pump. Throttling pump suction will cause pump cavitation. Here will cause the vacuum breaker to open whenever the pressure control valve open reduces to let the air in which is not desirable because increased O2 level in water will result in piping O2 corrosion.
I think that the system should be designed as Figure 2. In such an arrangement, the vacuum breaker will not open during normal operation.
What's your thought? I appreciate your input.
The system was designed to run 2, 3 or 4 pumps based on pump suction pond level and water user requirement. The system must keep certain pressure at the branch to send water to user 1.
The problem with figure 1 is that the section of the piping (sloped) downstream of the vacuum breaker is equivalent to a pump. Throttling pump suction will cause pump cavitation. Here will cause the vacuum breaker to open whenever the pressure control valve open reduces to let the air in which is not desirable because increased O2 level in water will result in piping O2 corrosion.
I think that the system should be designed as Figure 2. In such an arrangement, the vacuum breaker will not open during normal operation.
What's your thought? I appreciate your input.