bschlang
Civil/Environmental
- Oct 20, 2010
- 5
I'm not extremely familiar with WaterCAD v8 and working on a smaller commercial site that needs a service stub and fire hydrant. Existing infrastructure consists of a 16" main in the frontage road to the project with an 8" lateral stubbed at the project entrance.
I've set up a model with a reservoir at an elevation equal to 65 psi. The model goes, reservoir - 16" line - junction(1) - 8" line - junction(2) - 6" line - junction(3). Junction(3) has a small demand added to the system. I've run my typical scenarios and all the pressures stay within the reason of the 65 psi, everything looks good. Now to run my fire flow of 1500 gpm. I cannot get 1500 gpm at junction(2) or junction(3). This seemed unreasonable as the total distance from the 16" is less than 100 ft. It appears that my flow is being limited at junctions(2 & 3). For example I can only pull 780 gpm off junction(3).
I thought I should have adequate capacity to pull over 2500 gpm through a 6" pipe off an 8" off a 16", with sufficient capacity. I increased all the pipe sizes to 24" except the 6" and can still only pull 800 gpm off. It seems as though there is something limiting my amount of flow.
Any advice will be greatly appreciated. I don't know if WaterCAD has some limiting capabilities regarding dead ends and reservoirs. I've looped the system and was able to get greater flows, but it is not true representation of the model.
Thank you in advance.
Brett
I've set up a model with a reservoir at an elevation equal to 65 psi. The model goes, reservoir - 16" line - junction(1) - 8" line - junction(2) - 6" line - junction(3). Junction(3) has a small demand added to the system. I've run my typical scenarios and all the pressures stay within the reason of the 65 psi, everything looks good. Now to run my fire flow of 1500 gpm. I cannot get 1500 gpm at junction(2) or junction(3). This seemed unreasonable as the total distance from the 16" is less than 100 ft. It appears that my flow is being limited at junctions(2 & 3). For example I can only pull 780 gpm off junction(3).
I thought I should have adequate capacity to pull over 2500 gpm through a 6" pipe off an 8" off a 16", with sufficient capacity. I increased all the pipe sizes to 24" except the 6" and can still only pull 800 gpm off. It seems as though there is something limiting my amount of flow.
Any advice will be greatly appreciated. I don't know if WaterCAD has some limiting capabilities regarding dead ends and reservoirs. I've looped the system and was able to get greater flows, but it is not true representation of the model.
Thank you in advance.
Brett