I'm working on a project where the independent verifier has called into question the sliding resistance of one of our structures as our footings are on a waterproofing membrane. It is a portal frame type concrete structure on engineered fill with a friction angle of about 35 degrees.
Our engineer's calculations use tan(2/3)phi which basically means we're ignoring the waterproofing layer. The independent verifier is using a friction coefficient of about 0.25 because of the waterproofing layer.
My first thought was the if it moves any amount the membrane would be shredded anyway, but that argument falls over if waterproofing is required. Also if it moves the soil pressure will be relieved to Ka, but that's probably not going to help us either.
Does anyone know of any literature on the subject or how this is dealt with? I've been looking online but found nothing. We could just remove the waterproofing layer and use something like Xypex in the mix but I'd be interested to hear other points of view on this.
thanks
Our engineer's calculations use tan(2/3)phi which basically means we're ignoring the waterproofing layer. The independent verifier is using a friction coefficient of about 0.25 because of the waterproofing layer.
My first thought was the if it moves any amount the membrane would be shredded anyway, but that argument falls over if waterproofing is required. Also if it moves the soil pressure will be relieved to Ka, but that's probably not going to help us either.
Does anyone know of any literature on the subject or how this is dealt with? I've been looking online but found nothing. We could just remove the waterproofing layer and use something like Xypex in the mix but I'd be interested to hear other points of view on this.
thanks