Looking for the calculation which converts watts per sqare foot, to BTU then to refrigeration tonnage. Any help would appreciated.
 
Replies continue below

Recommended for you

Gentlemen you are forgetting the basics here !!!

You can not convert watts/ft[sup]2[/sup] to BTU because you can't compare power/area with energy Steven van Els
SAvanEls@cq-link.sr
 
In the UK we have gone through this conversion thing already, so here is typical conversions used

Power

kW -> BTU/hr(x 3412)
Tons Refrigeration -> kW (x 3.517)

Intensity of heat flow rate

BTU/hr square foot -> W/square metre (x 3.155)

Typically for budget cooling load estimating we use 140 W/square metre.

 