deetz
Electrical
- Nov 19, 2010
- 89
We are having some issues with voltage at our facility. We had the power company check the incoming and this is what they came up with. Does any of this make sense?
Sorry to send this to you on a Friday. Do you have an electrical engineer on staff? If not, you will probably need to contact a power quality consultant. You can give them the attached charts for reference.
The voltage and KVA are okay at the transformer; well within the voltage limits. You have the 5Th harmonic above 3% and the THD slightly above 5%. High 5th harmonics are usually from 6 pulse rectifiers. You also have a load that has sub cycle events above 1000 amps. You should hire a power quality electrical contractor Hunt / Olympia Tech. > Parsons > Etc.
Sorry to send this to you on a Friday. Do you have an electrical engineer on staff? If not, you will probably need to contact a power quality consultant. You can give them the attached charts for reference.
The voltage and KVA are okay at the transformer; well within the voltage limits. You have the 5Th harmonic above 3% and the THD slightly above 5%. High 5th harmonics are usually from 6 pulse rectifiers. You also have a load that has sub cycle events above 1000 amps. You should hire a power quality electrical contractor Hunt / Olympia Tech. > Parsons > Etc.