StLHokie
Structural
- Mar 27, 2018
- 8
Hi folks,
I'm currently working on a project that includes the design of a bridge crane runway girder. At this point in time, I've gotten news that (despite the runway girders already being fabricated and constructed on site) the bridge crane that will be used has increased significantly in size. The original maximum wheel load was around 7 kips, however the new maximum wheel load is now closer to 12 kips.
I originally oversized the beam a bit to provide some margin in case things changed, however that topped out at around 9 kips, the limiting failure mode being web sidesway buckling.
Removing and replacing the beam with a web of larger thickness is not possible, as the roof assembly has already been constructed. Therefore I'm left to pursue web reinforcement, namely transverse stiffeners or doubler plates.
I'm having issues finding information on spacing requirements of transverse stiffeners for crane rails, as transverse stiffeners are usually used for non-moving loads. The limited information on spacing I have found has mostly been with regards to built-up plate girder requirements. The issue with using built up plate girder requirements is the reliance on tension field action, which requires a weld of the stiffener to the bottom flange. From what I've been able to find, it isn't recommended to weld the stiffeners to the bottom flange for runway girders due to fatigue loading issues, so I'm not sure I can follow that line of methodology for spacing of the stiffeners.
Nothing I've been able to find in AISC/CMAA74/etc has gone into much of a discussion about the load distribution of a compression load longitudinally along a beam, other than J10.8 (AISC 14th) where there is brief discussion about web inclusion in the compression capacity. (But still not enough)
Depending on if I can find any other leads on stiffener spacing requirements, my other option would be to pursue web doubler plates. I, admittedly, have not researched this as thoroughly, however I have not found much in terms of standard practice in reinforcing existing beams. From my understanding doubler plates are typically much more useful for shear reinforcement of the web. Since web sidesway buckling is not exactly a shear failure, I'm not sure how effective a doubler plate would be. My thoughts are that the web and doubler plate would both buckle out plane due to the connection between the two only being at the location of the welds on the top and bottom of the plate (rather than the whole interface between the two).
Has anyone worked on anything like this before/have any leads? I can provide sketches and diagrams if what I've explained isn't clear enough. Thanks for the help!
I'm currently working on a project that includes the design of a bridge crane runway girder. At this point in time, I've gotten news that (despite the runway girders already being fabricated and constructed on site) the bridge crane that will be used has increased significantly in size. The original maximum wheel load was around 7 kips, however the new maximum wheel load is now closer to 12 kips.
I originally oversized the beam a bit to provide some margin in case things changed, however that topped out at around 9 kips, the limiting failure mode being web sidesway buckling.
Removing and replacing the beam with a web of larger thickness is not possible, as the roof assembly has already been constructed. Therefore I'm left to pursue web reinforcement, namely transverse stiffeners or doubler plates.
I'm having issues finding information on spacing requirements of transverse stiffeners for crane rails, as transverse stiffeners are usually used for non-moving loads. The limited information on spacing I have found has mostly been with regards to built-up plate girder requirements. The issue with using built up plate girder requirements is the reliance on tension field action, which requires a weld of the stiffener to the bottom flange. From what I've been able to find, it isn't recommended to weld the stiffeners to the bottom flange for runway girders due to fatigue loading issues, so I'm not sure I can follow that line of methodology for spacing of the stiffeners.
Nothing I've been able to find in AISC/CMAA74/etc has gone into much of a discussion about the load distribution of a compression load longitudinally along a beam, other than J10.8 (AISC 14th) where there is brief discussion about web inclusion in the compression capacity. (But still not enough)
Depending on if I can find any other leads on stiffener spacing requirements, my other option would be to pursue web doubler plates. I, admittedly, have not researched this as thoroughly, however I have not found much in terms of standard practice in reinforcing existing beams. From my understanding doubler plates are typically much more useful for shear reinforcement of the web. Since web sidesway buckling is not exactly a shear failure, I'm not sure how effective a doubler plate would be. My thoughts are that the web and doubler plate would both buckle out plane due to the connection between the two only being at the location of the welds on the top and bottom of the plate (rather than the whole interface between the two).
Has anyone worked on anything like this before/have any leads? I can provide sketches and diagrams if what I've explained isn't clear enough. Thanks for the help!