Weeping tile design

Status
Not open for further replies.

cht13er

Civil/Environmental
Jul 14, 2010
33
Been asked to conceptually design a weeping tile around a large (1000x750' or 325x230m) warehouse. Any suggestions as to where I should start?

Thanks in advance!
Chris
 
Replies continue below

Recommended for you

What is the condition of the groundwater? Draining a lake or a desert? Typically use 300' as a max run with laterals at 100' max... works fine in our environs but, we don't have much groundwater.

I'll post my notes for drainage, later.

Dik
 
Building is founded on several metres of compacted fill consisting primarily of silty sand. GWT approx 10m below the building.
 
For groundwater that low, why do you need it? Is it only to handle building runoff? If so, I agree with dik; except that I would cut the length of runs even lower.

If this is for roof runoff from collectors or downspouts, I'm not a fan of "hiding" the runoff. If an underdrain becomes clogged (and with silty sand surrounding it, there's a good chance of that), the water will backup and cause damage to the downspouts, the roof, or the structure.

I would create a series of "dry wells" lined with filter fabric and filled with gravel at or near each outlet and let the water drop into there.
 
Ron, thanks for your comments. The weeper is just to ensure the long-term performance of the foundation - the thought being that if they're sitting in a wet trench something could happen. Roof drains, as you suggest, will be directed to infiltration areas far away from the building.

My ignorance comes to the fore: dik said "300' max run with laterals at 100' max": what is a lateral? I cannot connect the weepers to the on-site storm sewers, as I'm designing parking lot storage: there's no free outlet. "300' max run" means that I could go 600' between sump pumps??

Thanks again!
Chris
 
Added info, I usually run perf pipe a max 300' before it changes direction of slope... this varies and for residential const, I usually use 40' to 50'. For a large warehouse without lots of ground water, 300' is OK.

Laterals are the drain tiles connecting the perf pipes to the sump (or, free drainage).

I usually determine the number of sump pumps from the water condition and/or the size. If problem water, then I often use 2 for redundancy, even for a small area.

The longer the run, the deeper the trench excavation and you should keep this above the lowest point of discharge <<++G++>>.

The attached are part of my General Notes (now over 300k in size). They are modified for each project and, depending on the use, have been upgraded for [Imperial | Metric]

Good luck...

Dik
 