Hello all,
I am involved in a LV system design I have sketched up in the attachment. Please open.
Discrimination at all levels is a requirement, but is difficult to achieve because the 270 main switch rating is so close to the 200 submain settings.
My design had a 2-off 160 CBs to each submain which discriminated with the 270 upstream.
The final design is shown in the sketch attached. Discrimination is achieved only for the subcircuits in each MDB. The engineer responsible rationalised that a fault upstream of these circuits is sufficiently unlikely that discrmination is not required.
What do you think of this compromise? opinions?
Michael.
I am involved in a LV system design I have sketched up in the attachment. Please open.
Discrimination at all levels is a requirement, but is difficult to achieve because the 270 main switch rating is so close to the 200 submain settings.
My design had a 2-off 160 CBs to each submain which discriminated with the 270 upstream.
The final design is shown in the sketch attached. Discrimination is achieved only for the subcircuits in each MDB. The engineer responsible rationalised that a fault upstream of these circuits is sufficiently unlikely that discrmination is not required.
What do you think of this compromise? opinions?
Michael.