ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
We have a strange condition wherein, our 600V switchgear power circuit breaker is tripping at no fault condition.
Here is the current case:
The switchgear is a main-tie-main with N.O. bus tie circuit breaker. The breaker is an 1600A K-Line breaker with solid state trip unit. The relay internal trip unit operates a lockout relay which in turn blocks closing of the the NO tie breaker. The tie breaker can be manually operated by close command pushbutton provided either or both incomer breakers are open and there is no lockout relay trip.
Automatic open transition transfer occurs when there is undervoltage or no no voltage at the line side of either incomer circuit breaker and no lockout trip.
Weird condition.
The incomer breaker A trips with no fault...the reason being is that the lockout relay did not operate nor the breaker registers a trip alarm indication. Because of this, the tie breaker can be closed locally/manually.
Is there any experience here for such weird condition? The breaker was replaced with a new one and still behaves the same way.
We have a strange condition wherein, our 600V switchgear power circuit breaker is tripping at no fault condition.
Here is the current case:
The switchgear is a main-tie-main with N.O. bus tie circuit breaker. The breaker is an 1600A K-Line breaker with solid state trip unit. The relay internal trip unit operates a lockout relay which in turn blocks closing of the the NO tie breaker. The tie breaker can be manually operated by close command pushbutton provided either or both incomer breakers are open and there is no lockout relay trip.
Automatic open transition transfer occurs when there is undervoltage or no no voltage at the line side of either incomer circuit breaker and no lockout trip.
Weird condition.
The incomer breaker A trips with no fault...the reason being is that the lockout relay did not operate nor the breaker registers a trip alarm indication. Because of this, the tie breaker can be closed locally/manually.
Is there any experience here for such weird condition? The breaker was replaced with a new one and still behaves the same way.