Weld 14 ga metal

Status
Not open for further replies.

break80

Structural
Mar 22, 2005
3
What would be the correct way to weld a 14 ga metal hanger (galvanized) to a 1/4" steel (Fy=36ksi) plate?
 
Replies continue below

Recommended for you

Drill a hole through the plate, stick the wire through, and bend it over. Knot it if you like.

If you insist on welding, grind off the zinc first, or suffer metal fume poisoning.



Mike Halloran
Pembroke Pines, FL, USA
 
Many of the Simpson galvanized hangers can be welded. Simpson has these notes for welding “Welds must conform to the current A.W.S. D1.3 structural welding code for sheet steel and must be performed by certified welder.” and “Welding galvanized steel may produce harmful fumes; follow proper welding procedures and safety precautions. Welding should be in accordance with (AWS) standards. Unless otherwise noted Simpson Strong-Tie connectors cannot be welded.”

Garth Dreger PE - AZ Phoenix area
As EOR's we should take the responsibility to design our structures to support the components we allow in our design per that industry standards.
 
kondrat...let's assume first that you are in the US and the applicable codes are AWS D1.3 and AWS D1.1 as woodman88 has noted.

The welders must be certified to both code provisions. D1.3 is sometimes more difficult to certify than D1.1.

Depending on the configuration of the connection, the certification must be for either fillet conditions or plug conditions. In qualification on sheet steel, they are similar.

 
I typically specify E60 (60 ksi) weld rods for welding to cold-formed steel.
 